Minimum copper THHN feeder size for 12 EVSEs rated at 24 amperes on a 3-phase, 4-wire, 120/208-volt system, assuming four EVSE per phase? (Use 1.732 for the square root of 3.)

Prepare for the Electric Vehicle Infrastructure Training Program Test. Use flashcards and multiple choice questions with hints and explanations. Get ready for your EVITP exam!

Multiple Choice

Minimum copper THHN feeder size for 12 EVSEs rated at 24 amperes on a 3-phase, 4-wire, 120/208-volt system, assuming four EVSE per phase? (Use 1.732 for the square root of 3.)

Explanation:
The situation tests how to size a three‑phase feeder when the loads are connected line‑to‑line, not line‑to‑neutral. In a 120/208 V system, if each EVSE is tied between two hot legs and draws 24 A, each unit delivers about 208 V × 24 A ≈ 4,992 W. With twelve EVSEs, the total power is about 12 × 4,992 ≈ 59,904 W. For a balanced three‑phase system, the line current is I = P total / (√3 × V line‑to‑line). Using √3 ≈ 1.732 and V_LL = 208 V gives I ≈ 59,904 / (1.732 × 208) ≈ 166 A. Copper THHN ampacities at 75°C show that 2/0 AWG has about 165 A, which would be just short of 166 A, while 4/0 AWG provides around 230 A, comfortably exceeding the 166 A requirement. Therefore, the minimum copper THHN feeder size is 4/0 AWG. The other options either exceed what’s needed (larger conductors) or fall short of the calculated requirement (2/0 AWG isn’t enough for 166 A).

The situation tests how to size a three‑phase feeder when the loads are connected line‑to‑line, not line‑to‑neutral. In a 120/208 V system, if each EVSE is tied between two hot legs and draws 24 A, each unit delivers about 208 V × 24 A ≈ 4,992 W. With twelve EVSEs, the total power is about 12 × 4,992 ≈ 59,904 W.

For a balanced three‑phase system, the line current is I = P total / (√3 × V line‑to‑line). Using √3 ≈ 1.732 and V_LL = 208 V gives I ≈ 59,904 / (1.732 × 208) ≈ 166 A.

Copper THHN ampacities at 75°C show that 2/0 AWG has about 165 A, which would be just short of 166 A, while 4/0 AWG provides around 230 A, comfortably exceeding the 166 A requirement. Therefore, the minimum copper THHN feeder size is 4/0 AWG.

The other options either exceed what’s needed (larger conductors) or fall short of the calculated requirement (2/0 AWG isn’t enough for 166 A).